Honeywell T7351 Product Data page 9

Commercial programmable thermostat for single- or multi-stage conventional/heat pump systems
Hide thumbs Also See for T7351:
Table of Contents

Advertisement

Text
Default
Choices
OATSENS 0
0 - 1
DATSENS 0
0 - 1
HUMSENS 0
0 - 2
OCCSENS 0
0 - 1
FAN HT
0
0 - 1
XFAN HT
YES
YES or NO
XFAN CL
NO
YES or NO
STRTDEL 0
0 - 15
ADVANCE NO
YES or NO
TMP LIM
3
0 - 5
TMP OCC 3
1 - 8
TMP CAL
0
-4 - 3
MINCOOL 45° F
45° - 99° F
(7° C)
(7° - 37° C)
MAXHEAT 90° F
40° - 90° F
(32° C)
(4° - 32° C)
HEATLCK NO
YES or NO
HTLCKSP 70° F
-40° - 120 ° F
(21° C)
(-40° - 49° C)
COOLLCK NO
YES or NO
CLLCKSP 35° F
-40° - 120° F
(2° C)
(-40° - 49° C)
DAT LL
NO
YES or NO
DATLLSP
45° F
35° - 60° F
(7° C)
(2° - 16° C)
Table 5. Installer Setup. (Continued)
Outdoor Air Sensor Selection
0: None
1: Remote Outdoor Air Sensor
Discharge Air Sensor Selection
0: None
1: Remote Discharge Air Sensor
Room Humidity Sensor selection
0: None
1: On Board Sensor
2: Remote Sensor
Occupancy Sensor Selection
0: None
1: Remote Occ Sensor
Fan Operation on Heat
0: Conventional (Equipment controls Fan)
1: Electric (Thermostat turns on Fan with call for Heat)
Extended Fan on Heat
NO: None
YES: 90 seconds
Extended Fan on Cool
NO: None
YES: 40 seconds
Sequential Start Delay
0 to 150 seconds in 10 second increments
Advanced Settings
NO: Hide
YES: Show
Temporary Setpoint Adjustment
0: 0 Deg. F
1: 1 Deg. F
2: 2 Deg. F
3: 3 Deg. F
4: 4 Deg. F
5: 5 Deg. F
Temporary Occupied Duration
1 to 8 hours
Temporary Display Adjustment
0 - 3 = 0 to 3 DDF
4 - 7 = -4 to -1 DDF
Min Cool Setpoint
Max Heat Setpoint
Heating Lockout (Only displayed if Outdoor Air Sensor is selected)
NO: None
YES: Enabled
Heating Lockout Temperature
(Display only if Remote Outdoor Air Sensor is configured)
Cooling Lockout (Only displayed if Outdoor Air Sensor is Selected)
NO: None
YES: Enabled
Cooling Lockout Temperature
(Display only if Remote Outdoor Air Sensor is configured)
Discharge Low Limit (Only displayed if Discharge Air Sensor is Selected)
NO: None
YES: Enabled
Discharge Low Temp Limit
(Display only if Discharge Sensor is configured)
9
T7351 COMMERCIAL PROGRAMMABLE THERMOSTAT