T7351 COMMERCIAL PROGRAMMABLE THERMOSTAT
Text
Default
XFAN HT
YES
YES or NO
XFAN CL
NO
YES or NO
STRTDEL
0
0 - 15
ADVANCE NO
YES or NO
TMP LIM
3
0 - 5
TMP OCC 3
1 - 8
TMP CAL
0
-4 - 3
MINCOOL 45° F
45° - 99° F
(7° C)
(7° - 37° C)
MAXHEAT 90° F
40° - 90° F
(32° C)
(4° - 32°)
HEATLCK
NO
YES or NO
HTLCKSP 70° F
-40° - 120 ° F
(21° C)
(-40° - 49° F)
COOLLCK NO
YES or NO
CLLCKSP
35° F
-40° - 120° F
(2° C)
(-40° - 49° C)
DAT LL
NO
YES or NO
DATLLSP
45° F
35° - 60° F
(7° C)
(2° - 16° C)
DAT HL
NO
YES or NO
DATHLSP
110° F
65° - 140° F
(43° C)
(18° - 60° C)
DEHUMID 0
0 - 5
DEH MIN
5
5 - 15
DEH TMP
2
1 - 5
MINHTRT
5
0 - 20 DDF/HR Minimum Heat Recovery Ramp Rate
MAXHTRT 8
0 - 20 DDF/HR Maximum Heat Recovery Ramp Rate (Only Displayed if Outdoor Sensor is
MINHTOA 0° F
-20° - 120° F
(-18° C)
(-29° - 49° C)
62-0258
Table 3. Installer Setup. (Continued)
Choices
Extended Fan on Heat
NO: None
YES: 90 seconds
Extended Fan on Cool
NO: None
YES: 40 seconds
Sequential Start Delay
0 to 150 seconds in 10 second increments
Advanced Settings
NO: Hide
YES: Show
Temporary Setpoint Adjustment
0: 0 Deg. F
1: 1 Deg. F
2: 2 Deg. F
3: 3 Deg. F
4: 4 Deg. F
5: 5 Deg. F
Temporary Occupied Duration
1 to 8 hours
Temporary Display Adjustment
0 - 3 = 0 to 3 DDF
4 - 7 = -4 to -1 DDF
Min Cool Setpoint
Max Heat Setpoint
Heating Lockout (Only displayed if Outdoor Air Sensor is selected)
NO: None
YES: Enabled
Heating Lockout Temperature
(Display only if Remote Outdoor Air Sensor is configured)
Cooling Lockout (Only displayed if Outdoor Air Sensor is Selected)
NO: None
YES: Enabled
Cooling Lockout Temperature
(Display only if Remote Outdoor Air Sensor is configured)
Discharge Low Limit (Only displayed if Discharge Air Sensor is Selected)
NO: None
YES: Enabled
Discharge Low Temp Limit
(Display only if Discharge Sensor is configured)
Discharge High Limit (Only displayed if Discharge Air Sensor is Selected)
NO: None
YES: Enabled
Discharge High Temperature Limit
(Display only if Discharge Sensor is configured)
Dehumidification
0: None
1: MinOn Time
2: Reset Temp Setpoint
3: Reset w/ MinOn
4: Reheat
5: Reheat w/ Min On
Dehumidify Minutes On
Dehumidify Temp Reset
Selected)
Minimum Heat Outdoor Air Temperature (Only Displayed if Outdoor Sensor is
Selected)
Notes
6